Need info: 1200 amp 480/277V disconnect

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I only need round numbers. What would be the likely dimensions (H, W, D), the weight, and the cost (material only) of an outdoor-rated,1200 amp, 480/277V disconnect? It would be installed on a pad adjacent to the pad for the utility transformer. Alao, since the service switchboard would be some distance away on its own outdoor pad, would the disconnect need to be fused?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The disconnect will be the service disconnect, and will need to have fuses. Even if you find away to not have the disconnect be the service disconnect, you will still likely need fuses as most non-fused disconnects have a SCCR of 10kA.
List price shows at about $20k
Depth17.75 in (450.85 mm)
Width36.62 in (930.15 mm)
Height69.13 in (1755.90 mm)
Net Weight382.06 lb(US) (173.3 kg)
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
What is the disconnect for?
"Convenience."

There will be a significant delay between setting the utility transformer and installing the service lateral and everything else downstream. The PM is hoping that having their own disconnecting means immediately adjacent to the transformer will allow the contractor to energize the system without having to wait for the utility to turn off then turn on their transformer. Whether or not PSE will go along with this idea is yet to be seen.
 

kwired

Electron manager
Location
NE Nebraska
If purchasing as stand alone item I'd expect different price than if purchased with the mentioned switchboard that it is supplying.
These manufacturers like to sell items by the job and you get different pricing when purchasing the whole job than if you purchased every item as a separate purchase, usually much better pricing. You likely don't get line item pricing on such orders but the lump sum is still much less than separately purchasing all the items.
 
"Convenience."

There will be a significant delay between setting the utility transformer and installing the service lateral and everything else downstream. The PM is hoping that having their own disconnecting means immediately adjacent to the transformer will allow the contractor to energize the system without having to wait for the utility to turn off then turn on their transformer. Whether or not PSE will go along with this idea is yet to be seen.
That's a lot of expense for a one time convenience 🤔
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The disconnect will be the service disconnect, and will need to have fuses. Even if you find away to not have the disconnect be the service disconnect, you will still likely need fuses as most non-fused disconnects have a SCCR of 10kA.
List price shows at about $20k
Depth17.75 in (450.85 mm)
Width36.62 in (930.15 mm)
Height69.13 in (1755.90 mm)
Net Weight382.06 lb(US) (173.3 kg)
That’s for a 1200A fusible “safety switch”, aka knife switch. 1200A is the upper limit of that technology.

If you need GF protection, you need a switch that can be fitted with a shunt trip, so it becomes a “bolted pressure switch” (BPS), also known as a “Pringle Switch”. That will run you about $90k, figure 40W x 36D x 92H.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The issue has gone away. PSE, understandably, won't go along with the idea of providing power to a disconnect switch before their metering is installed in the downstream switchboard (scheduled to take place many months later).

One more question: if there was a disconnect immediately downstream of the transformer, would I be right in saying the wires from the transformer to the disconnect comprise a "service lateral" and the wires from the disconnect to the switchboard comprise a "feeder"?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
The issue has gone away. PSE, understandably, won't go along with the idea of providing power to a disconnect switch before their metering is installed in the downstream switchboard (scheduled to take place many months later).

One more question: if there was a disconnect immediately downstream of the transformer, would I be right in saying the wires from the transformer to the disconnect comprise a "service lateral" and the wires from the disconnect to the switchboard comprise a "feeder"?
Around here there service point would be the transformer terminals...

The wires from the transformer to the disconnect would be service entrance conductors.

The wires from the disconnect to the switchboard would be a feeder.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The issue has gone away. PSE, understandably, won't go along with the idea of providing power to a disconnect switch before their metering is installed in the downstream switchboard (scheduled to take place many months later).

One more question: if there was a disconnect immediately downstream of the transformer, would I be right in saying the wires from the transformer to the disconnect comprise a "service lateral" and the wires from the disconnect to the switchboard comprise a "feeder"?
The conductors on the load side of the disconnect would be feeder conductors. The conductors between the transformer and the disconnect would be either service laterals or underground service conductors depending on the location of the service point.
 