Electric-Light
Senior Member
I'm aware that the voltage of any conductor must not surpass the lowest rating of a breaker to satisfy the NEC in countries adopting that set of codes, but that aside, I am wondering if equipment are meant to handle it. I know that computers are fine as the world spec power supplies are designed to take it all with no regard to grounding polarity but what about other 208-240v stuff?
Using some fairly common examples in the US, there are corner ground 240v with A phase grounded giving 240v between A-B and B-C.
A-B and A-C provides single ended power just like European domestic power and American 277v lighting power.
B-C provides 240v to ground on either sides and between lines and requires a double pole breaker.
French non-directional type items should be ok on all and almost all European items should be fine on the A-B, A-C setup, but what about American 208/240v items such as water heater, A/C condensing units, etc? Are they UL rated for any parts of internal components having a potential of over 120v to the ground? Is the 240:24v transformer that feeds the living quarters rated to have 208 or 240v of potential between windings?
What about the effect on the TVSS used in BLDC drivers? Minisplits, ECMs (motor) utilize them. I understand that if the TVSS parts were all designed to accept 240v to ground, it would not provide effective common mode suppression on a system that is only 120v to the ground.
What about the legality? The shock of a 240v L-N system is just like that of 277v.
Another one we have is this kind:
A-C gets you 240v just like residential power with 120v to the ground. A-B or B-C however gets you 120v on one side and 208v to ground on the other.
Using some fairly common examples in the US, there are corner ground 240v with A phase grounded giving 240v between A-B and B-C.
A-B and A-C provides single ended power just like European domestic power and American 277v lighting power.
B-C provides 240v to ground on either sides and between lines and requires a double pole breaker.
French non-directional type items should be ok on all and almost all European items should be fine on the A-B, A-C setup, but what about American 208/240v items such as water heater, A/C condensing units, etc? Are they UL rated for any parts of internal components having a potential of over 120v to the ground? Is the 240:24v transformer that feeds the living quarters rated to have 208 or 240v of potential between windings?
What about the effect on the TVSS used in BLDC drivers? Minisplits, ECMs (motor) utilize them. I understand that if the TVSS parts were all designed to accept 240v to ground, it would not provide effective common mode suppression on a system that is only 120v to the ground.
What about the legality? The shock of a 240v L-N system is just like that of 277v.
Another one we have is this kind:
A-C gets you 240v just like residential power with 120v to the ground. A-B or B-C however gets you 120v on one side and 208v to ground on the other.