We have a design and build on a 5000 sq ft doctors office here in Texas. The service is 120/208v 3 phase. Connected amps are 759 which puts me just under the 10% mark for an 800a service. I need to find another 10 or 11% Any of you with hvac experince feel like 5 15kva heat units on this building is a bit excessive? 75kva for this size building seems pretty high to me. Thoughts?:?
	
		
			
		
		
	
				
			
			