I have received some electrical drawings on a Industrial cabinet.  I noticed on the 480v 3phase, they have 5 motors on a 30amp fuse.  But 
the motors ratings are as follows: 12.2A , 10.32A, 10.32A, .9A, and 8.39A. With the 125% I am seeing that it needs 60Amp fuse. Please advice.
Danke
Ron
	
		
			
		
		
	
				
			the motors ratings are as follows: 12.2A , 10.32A, 10.32A, .9A, and 8.39A. With the 125% I am seeing that it needs 60Amp fuse. Please advice.