In OP case, it is a fan(causing him headache). A motor driving a fan will not be damaged by low voltage.
Maybe, maybe not.
If the shaft load is 'X' horsepower, the motor doesn't know if it's a fan or something else.
In OP case, it is a fan(causing him headache). A motor driving a fan will not be damaged by low voltage.
If the shaft load is 'X' horsepower, the motor doesn't know if it's a fan or something else.
golddigger, they are R-410 units, have been for many years. It seems to be as good as R-22.
electriclight, not installed to the letter of the manual, but none are and they all work fine. the air is plenty cold; the front fan just doesnt move it well enough.
With fan type load, torque required decreases with speed and so horsepower. With constant torque loads, the reduction in horsepower is small.
Well, this is a plausible symptom if the installation practice deviation from the manual is something that might affect the airflow. You could get a 120v to 240v travel transformer and run both fans from an outlet just to confirm if a transformer would do anything while letting the compressor run on original circuit. Since 200v under load is within the ANSI tolerance for 208v service, if this fixes the issue, it's a manufacturer's issue. This is assuming installation deviation doesn't affect air flow. (like clearance on the back, sides, proper placement in wall)
I don't know the specific piece of equipment but also check diagrams in the cabinet that there's no taps for 208 vs 230v. Such a tap is common in kitchen equipment.
Hi, JF, have you checked the rated CFM for the air conditioner with an air flow meter? It may be given in the unit manual. A thumb rule is 400 CFM/TR.
Do not try to oversize the capacitor lest it should increase the current in the winding beyond its capacity.
That is what I have noticed in hotel rooms. Turn the unit down and it will be cool near the unit, cool enough the thermostat isn't calling for cooling, but not sufficient enough air flow to mix the air throughout the room. Given enough time the other end of the room will cool down, this sort of works if you leave the temp set and don't adjust it constantly. In hotel room housekeeping likely changes it back to wherever they are told to set it whenever guests check out, and the room never really stabilizes in temperature.I have not tho I know it's low. I believe factory specs are 280/340 CFM for low/high speed. The opening is roughly 2" x 2', and due to the design of the fan, airflow is uniform across that opening. 340CFM/.4 ft2 = 850ft/min, or 14.2fps, or 9.7mph. I'll need exact duct measurements of course. Standing 5' in front of the unit, you cannot feel the air coming out. I've also tried orienting the grill both ways (more out vs up and vice-versa).
These units have a local (unit mounted) thermostat. It'll be 60* at the PTAC and 80* across the room. Units simply dont blow air far or hard enough away to cool the room uniformly. I'll have some new 2uf caps in the morning, will see if that solves the issue.
That is what I have noticed in hotel rooms. Turn the unit down and it will be cool near the unit, cool enough the thermostat isn't calling for cooling, but not sufficient enough air flow to mix the air throughout the room. Given enough time the other end of the room will cool down, this sort of works if you leave the temp set and don't adjust it constantly. In hotel room housekeeping likely changes it back to wherever they are told to set it whenever guests check out, and the room never really stabilizes in temperature.
Window shakers aren't really much different - cool near the unit warm across the room.
Discharge air and return air are so close to one another you mostly recirculate the same air through the unit, especially when mounted close to the floor as colder discharge air will tend to fall to the floor and that is the air taken back through the return.
You need ceiling fans to stir the air up and even the room temp.