Need some feedback on a question of safety...

Status
Not open for further replies.

Fulthrotl

~Autocorrect is My Worst Enema.~
here's the deal.... one of my commercial accounts is a roofing contractor
who calls me when they are doing a tilt up, and need protection around
a weatherhead or service drop so that nobody on the crew gets fried.

i got an email today that looks like this:

==============================
Hi Randy
I was wondering if I could get a price from you to wrap these
wires for us. I'm pretty sure that you could do everything from
the roof. There are 2 sets of 3 wires. Let me know if you can
give me a price from the photos or if you would have to see the
job. The job is near 110 fwy and Martin Luther King Blvd in LA.
=============================

here's a couple photos of the work....

WestenUnifiedBakery008.jpg


WestenUnifiedBakery004.jpg


now, i'm looking at the cans on the crossbar, and they look awfully
close to the edge of the building... close enough that a roof finisher
with a roller on a 12' aluminum paint pole is a huge risk of contacting
secondary or primary, which appears to be 5kv.

my solution that seems safe, is to put up 10' 2x8's on the outside of the
building, every 2', anchored with 1/2" readheads , with 6' above the
parapet, and 4' below the parapet, and put 1/2" 4x8 plywood vertically,
so there is an 8' tall barrier along the edge of the building where the
poles, crossbar, and transformers are at. and "PELIGRO, high voltage" signs.

one concern is wind load, and this needs to be secure so it doesn't
come loose if we get a good wind.

is an 8' barrier wall sufficient that unqualified personnel can be on
the other side of it?

any suggestons on this one that would be better, safer, or given
that california has lawyers on 16" centers thruout the state, should
i just let this one go?

thanks for any insight you may have.


randy
 

Buck Parrish

Senior Member
Location
NC & IN
I WAS THINKING A PLYWOOD WALL AS SOON AS I SEEN IT.

I would call the poco and have them do some thing. Unless you need the work.
That looks like a dangerous situation
 

wireguru

Senior Member
i would definitely call the poco (LADWP?) have have them sleeve the primary lines. Ive also seen them with these big blanket things. Bottom line is poco needs to be involved. I wouldnt want the liability of an electrocuted roofer.
 

frizbeedog

Senior Member
Location
Oregon
wireguru said:
i would definitely call the poco (LADWP?) have have them sleeve the primary lines....... Bottom line is poco needs to be involved.

Agree.....unless you like dealing with their equipment or area of responsibility.

....or are you allowed to?
 

zog

Senior Member
Location
Charlotte, NC
wireguru said:
i would definitely call the poco (LADWP?) have have them sleeve the primary lines. Ive also seen them with these big blanket things. Bottom line is poco needs to be involved. I wouldnt want the liability of an electrocuted roofer.

I agree also, this is the best way to go.
 

charlie

Senior Member
Location
Indianapolis
As bad as it looks, I don't see any NESC violations. Keep in mind that California doesn't use the NESC but have written their own. The primary does appear to be 5 kV and the services are either corner grounded or are ungrounded. Anything the utility does would be billed to the customer if they do meet the California version of the NESC. :)
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
I actually thought that was a pic of a store in our town. We have the same situation, but somebody, could have been the POCO, put up a chain link backstop (for lack of a better word) to keep people away.

Now I would suggest anyone who is not familier with working around high voltage shouldn't try to put up a chain link fence.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
I actually thought that was a pic of a store in our town. We have the same situation, but somebody, could have been the POCO, put up a chain link backstop (for lack of a better word) to keep people away.

Now I would suggest anyone who is not familier with working around high voltage shouldn't try to put up a chain link fence.

thanks for all of your inputs.... it pretty much parallels my thoughts
on it... and as it's in LADWP service area.... i KNOW what their response
is... they will take out a clearance, shut down a line, or service drop,
place shorts and grounds, call it an outage. and bill accordingly.

they will NOT blanket service entrances or 5kv peddlers for outside
contractors and leave them energized.

the chain link barrier is a good permanent solution.... and that close to
a 5kv peddler, they are gonna make every fence pole be cadwelded to
a 4/0 ground cable, and that goes to a 500 mcm ground cable 2' down
in the dirt... just like a switchrack...
(i got stuck once cadwelding chain link fencing going around a switch rack)

DWP's position in their own areas, is that there MUST be an electrical
safety officer present when unqualified workers are near energized
equipment. he can perform no work, he is oversight only, and nobody
can work without him there.

all of you, thanks again for your help. time to go break the news to
my soon to be disappointed customer.


randy
 

peter d

Senior Member
Location
New England
DWP's position in their own areas, is that there MUST be an electrical
safety officer present when unqualified workers are near energized
equipment. he can perform no work, he is oversight only, and nobody
can work without him there.

all of you, thanks again for your help. time to go break the news to
my soon to be disappointed customer.


randy

Sounds ridiculous. Around here they will boot the HV and LV stuff and be done with it.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
Sounds ridiculous. Around here they will boot the HV and LV stuff and be done with it.

regardless of how it sounds, that is how LADWP operates.
i worked there for two years. it was an amazing experience.
not always in a good way.

i watched them throw out. not salvage, throw out a crate
of 316 SS nuts, bolts, belville washers that was 4'x8'x2' deep,
because it was too much work to sort them. most of them
1/2" -13 by varying length, from 1" to 5".

sometime i'll have to post the story how i, armed with a
single sheet of paper, and a pencil, almost caused the
engineering department to spend $600,000 on testing a
transformer that was being bowsered.

DWP=Deep Wide Pockets


randy
 

wireguru

Senior Member
regardless of how it sounds, that is how LADWP operates.
i worked there for two years. it was an amazing experience.
not always in a good way.

i watched them throw out. not salvage, throw out a crate
of 316 SS nuts, bolts, belville washers that was 4'x8'x2' deep,
because it was too much work to sort them. most of them
1/2" -13 by varying length, from 1" to 5".

sometime i'll have to post the story how i, armed with a
single sheet of paper, and a pencil, almost caused the
engineering department to spend $600,000 on testing a
transformer that was being bowsered.

DWP=Deep Wide Pockets


randy


more ladwp stories please :smile:
 

Fulthrotl

~Autocorrect is My Worst Enema.~
Well, since LADWP is the "Poco to the Hollywood Stars" you have to run your business just like your clientele lives their lives. I wouldn't expect it any other way. ;)

in order to support your assumptions, i've taken the liberty of including
a photo from the parking lot of the hotel Bel Air... we were doing a backup
temporary generator there, as they had a big weekend planned, and
didn't want a power outage.... they rolled out 3 meals a day to ensure
happy employees... we were happy.... double time on sunday, and it
was catered.... and what we did was watch a generator not run.
tough day.. sleeping in the cab, and having to get out and walk across