here's the deal.... one of my commercial accounts is a roofing contractor
who calls me when they are doing a tilt up, and need protection around
a weatherhead or service drop so that nobody on the crew gets fried.
i got an email today that looks like this:
Hi Randy
I was wondering if I could get a price from you to wrap these
wires for us. I'm pretty sure that you could do everything from
the roof. There are 2 sets of 3 wires. Let me know if you can
give me a price from the photos or if you would have to see the
job. The job is near 110 fwy and Martin Luther King Blvd in LA.
here's a couple photos of the work....
now, i'm looking at the cans on the crossbar, and they look awfully
close to the edge of the building... close enough that a roof finisher
with a roller on a 12' aluminum paint pole is a huge risk of contacting
secondary or primary, which appears to be 5kv.
my solution that seems safe, is to put up 10' 2x8's on the outside of the
building, every 2', anchored with 1/2" readheads , with 6' above the
parapet, and 4' below the parapet, and put 1/2" 4x8 plywood vertically,
so there is an 8' tall barrier along the edge of the building where the
poles, crossbar, and transformers are at. and "PELIGRO, high voltage" signs.
one concern is wind load, and this needs to be secure so it doesn't
come loose if we get a good wind.
is an 8' barrier wall sufficient that unqualified personnel can be on
the other side of it?
any suggestons on this one that would be better, safer, or given
that california has lawyers on 16" centers thruout the state, should
i just let this one go?
thanks for any insight you may have.
randy