I wasnt hired to upgrade I was hired to do the scope they provided lol were getting off track of the original question

Sent from my SM-G950U using Tapatalk
 
Yes we are. First time it’s ever happened.:)

:lol:

So do you all agree with my previous post? IMO the wording is still a bit vague as to whether the tap conductors need to terminate on a breaker for the 10 foot rule, but if they don't they must have an ampacity " not less than the rating of the device supplied by the tap conductors" which would be the MLO panelboard, so one would need 100 amp tap conductors min for a 100 amp panel.
 