Lineman1123
Member
- Location
- Boston, MA
So I have a 4 unit + common+ store+ 2 salons.
I cant get a meter for the next 1.5 years. Horrible I know you guys going through the same thing. It’s a 600 amp service.
Since I can’t get a meter box, the inspector wants me to put a 600 main disconnect outside, but I’m not sure how I can temporary supply power to the building/units while I wait for the meter box. Anyone have any ideas ? I thought I can out up single gang meters and just have separate risers for each one but the inspector shut me down on that because I need a 600 amp main disconnect for the service line coming in.
Guys im in a jam! Any help would be appreciated. I will post pictures tomorrow.
I cant get a meter for the next 1.5 years. Horrible I know you guys going through the same thing. It’s a 600 amp service.
Since I can’t get a meter box, the inspector wants me to put a 600 main disconnect outside, but I’m not sure how I can temporary supply power to the building/units while I wait for the meter box. Anyone have any ideas ? I thought I can out up single gang meters and just have separate risers for each one but the inspector shut me down on that because I need a 600 amp main disconnect for the service line coming in.