J Jim1959 Senior Member Location Longmont, CO Jan 15, 2019 #1 Is a Nema 1 wireway acceptable for use in Class I Div 2?
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Jan 15, 2019 #2 See Section 501.10(B)(1)(2).
J Jim1959 Senior Member Location Longmont, CO Jan 15, 2019 #3 Thank you, that's what I thought but could not get my eye on it. Always appreciate your timely replies.