Yes, for the individual starters. But in gasketed MCCs the wireway doors and covers are not sealed so there can still be quite a bit of dust ingress.... add significant dust resistance...
For stand alone devices NEMA 1 Gasketed may just mean the manufacturer never submitted it to, or it could not completely pass, a full Type 12 testing. After all, technically as soon as you punch any hole into a UL Listed enclosure, it becomes a Type 1 unless they 're-certify' it.
The reason why some VFD mfrs are adopting the NEMA "1G / 1A" terminology is because if you must ventilate a box, there is NO WAY it passes type 12 (or 4) test requirements. When the enclosure ratings were just supported by NEMA and compliance was voluntary, peoplee used to use the term NEMA "12-V" for Vented. This is a complete oxymoron, you cannot have a box that is sealed and vented at the same time, no matter how good you think your filters are.
Once UL took over the specifications and testing of enclosure type ratings, the concept of "12-V" was of course exposed as a fraud, and eliminated. So now the ONLY rating you can get on ANY enclosure that has any type of exposure to free air exchange is Type 1. So even if you start with a Type 4X stainless steel enclosure, if you put vents in it, the UL rating reverts to Type 1. So now when people ask for type 12 but vents are needed because it is a VFD, the only thing the mfr can safely say without it being a lie that could jeopardize their UL listing is to say it is Type 1, and they add the "A" or 'G" like the MCC people do to indicate that it is still gasketed.
there are now fans and grills that are UL listed as type 12 so it is indeed possible to ventilate a type 12 cabinet.
TFP Optional Grilles and Replacement Filters
Optional grilles offer the choice of stainless steel or black ABS plastic. These grilles replace the standard RAL 7035 gray composite or stainless steel grilles on both fan and exhaust packages. Standard replacement filters are washable foam (Type 1) or disposable (Type 12). To maintain UL Type 12 rating on the enclosure, UL Type 12 filters must be used on the fan package inlet. Washable aluminum filters are also available. Aluminum filters are compatible with Type 1 systems only.
Type 12 air filters are not washable.
[*]The fan is UL listed under UL508A, which does NOT address enclosure ratings. But still, it's a "true" statement that it is UL listed.
Hypothetically, what if instead of direct venting with filtering the air supply and return are ducted to outside the dust or moisture exposure area?I don't know what to think for certain about the rest of what was brought up on this topic, but depending on just what/where/how a vent is installed couldn't the enclosure possibly still meet 3R rating requirements? Types 4 and 12 are understandable one could lose those ratings if any air exchange is introduced at all.
Yes, the specs for 3R do not say that moisture will not enter, only that it will not get to live parts. That's why 3R enclosure need a weep hole of some sort.I don't know what to think for certain about the rest of what was brought up on this topic, but depending on just what/where/how a vent is installed couldn't the enclosure possibly still meet 3R rating requirements? Types 4 and 12 are understandable one could lose those ratings if any air exchange is introduced at all.
Looks ad though I allowed my bias to prevent me from seeing the changes. I had looked on Hoffman's site and did not see that though. Thanks for the wakeup call.Hoffman is one of the companies selling fans and grills that are UL listed as type 12.
http://www.hoffmanonline.com/produc...=2383&cat_3=138274&catID=138274&itemID=138532
Pfanneberg also offers type 12 fans.
http://www.pfannenbergusa.com/filterfan
I have used both of them. I doubt either of these companies would make up a UL listing claim they could not back up.
Incidentally, this is a fairly recent development. I never bought into the arguments a few vendors made about ventilation of type 12 enclosures in the past that you have mentioned. They were obvious to me because of the ambiguous phrasing. The phrasing being used now is very unambiguous.