Nema rating disconnect
hhsting
Glen bunie, md, us
Junior plan reviewer
I have disconnect inside walk in freezer. Quick question what is the typical nema rating for disconnect inside walk-in freezer?
Leave something unwrapped in a freezer and it will become dehydrated.
Disclaimer, I'm not saying they should be considered a dry location
OR type 6 or similar water-tight enclosures.
Why such extremes?
4X is for corrosive environments. Type 6 is for submersion at limited depth.
Any of the Type 3 version are rated for damp and operation with ice covered.
My preference would probably be a combination 3R/12 style, but forr a restaurant style operation any outdoor device would be okay.
Why such extremes?
My preference would probably be a combination 3R/12 style.
just options. they all work.
I don't know what they plan to do in the freezer. I have seen places do some food processing in freezers or hose them down occasionally. They needed disconnects for the processing equipment. NEMA 4 or 6.
If it is just dry freezer foods being stored like in a grocery store then it likely won't matter.
Never a need for Type 6 unless it is being submerged.
Typically a Type 4 meets most requirements, although finding a Type 4X is probably easier.
Until the door is left open, like during loading/unloading, then the humidity builds up pretty fast.
But does that humidity cause rain on your equipment inside? If it does, I could see requiring 3R, otherwise seems like Type 1 would suffice.
On the other hand, if that humidity can penetrate the equipment before condensing inside, maybe an enclosure type that would prevent the entrance of ambient air is appropriate?
Cheers, Wayne
I have seen some Nema 1 enclosures fully rusted or pitted out in walk-ins / cold rooms. But it was industrial and there was discussion that the area was being hosed down or brought to room temp daily creating condensation on the terminals and wires.
Non-metallic makes sense for these type of environment. Personally, I don't like any electrical in most small walk-in freezers
Cheers, Wayne
Would not nema 4X be good for walkin freezer in restaurant or nema 3R? Which?
Use NEMA 3 which is overkill but will have you covered. If you get a chance, go into a walk in freezer and look at the evaporator(s), their wiring is open and NEMA 1 at best.
The OP's job is as a plan reviewer. So the question is whether a NEMA 1 disconnect (or lack of specification on the plans requiring something other than NEMA 1) should be rejected at plan review or not.
Cheers, Wayne