wireday
Senior Member
- Location
- New England
- Occupation
- Master electrician
So devil's advocate here..... Under what code section would you see that as allowed? 400.7(A)(8)?It can't be any worse than hard-wiring it.
Lemme take a look.So devil's advocate here..... Under what code section would you see that as allowed? 400.7(A)(8)?
Sorry, old code reference.....just looking at uses permitted and not permitted, 400.10 and 12.... Seems like we have to find something in 400.10 uses permitted that makes this acceptable. 400.10(A) 6,7,8 all seem like a stretch to me for this application.Lemme take a look.
I'm back. My '17 doesn't even have a 400.7.
I have a 400.10 (uses permitted) and a 400.12 (uses not permitted).
What do you see as prohibiting it?
What do you see as prohibiting it?
Larry, can you reread post #7. What do you see applying under "uses permitted"?To repeat myself:
The only objection I can imagine, and it's really nitpicking, is 412(4), the use of the 1/2" 1-hole strap.
Do you have a reason the believe the enclosure needs to be supplied by a hard-wired method?
Okay, I'm with you. I'm not sure why this use of a cord would fall under NEC jurisdiction at all.Larry, can you reread post #7. What do you see applying under "uses permitted"?
Okay, I'm with you. I'm not sure why this use of a cord would fall under NEC jurisdiction at all.
Is it because the enclosure is attached to the wall? Does the NEC cover every cord in every use?
Here is my take:. I don't see any reason why the NEC wouldn't apply to this. IMO, the only time it wouldn't would be a factory installed cord on a piece of (probably listed) equipment. I'm sure we remember Mike holt's argument that power cords on factory equipment are listed items under power cord sets or something like that so they not covered by the NEC. I suppose there are a few gray areas like if I replace say a damaged factory cord with an article 400 cord and a cord cap, then what?Doesn't the answer depend on what's inside the cabinet? E.g. if the cord is the end of a power strip inside the cabinet, supplying various network equipment, how is that a problem? Vs a device box mounted inside the cabinet, with a regular receptacle in it, maybe the cord is an issue.
Cheers, Wayne
This one in the first picture is hard wired, I was asked to add strain relief to another network box that has power strip and plugs, What would you recommend in this case?Doesn't the answer depend on what's inside the cabinet? E.g. if the cord is the end of a power strip inside the cabinet, supplying various network equipment, how is that a problem? Vs a device box mounted inside the cabinet, with a regular receptacle in it, maybe the cord is an issue.
Cheers, Wayne
Are you saying that one is never allowed to make any kind of assembly and attach a power cord to it?If that was a factory cord on say a wifi router, I would say no NEC. But that is clearly not a factory cord, so unless possibly that was a repair as I mentioned in the previous paragraph, seems to me the NEC would apply.
Sure you can, but IMO then it would fall under the NEC, and be subject to the provisions of article 400, such as the "not used for permanent wiring" and uses permitted sections.Are you saying that one is never allowed to make any kind of assembly and attach a power cord to it?
Then I'm circling back to still not seeing the OP's application as a substitute for permanent wiring.Sure you can, but IMO then it would fall under the NEC, and be subject to the provisions of article 400, such as the "not used for permanent wiring" and uses permitted sections.