winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
If you have a wye source, and a MWBC supplying an A-B load and a C-N load, and all phases are loaded to the same current, then the N will carry as much current as the phases.
Similarly if you have a wye source and an MWBC supplying loads which have different power factors, you could have a situation where N will carry as much current as the phases.
In these situations the physics suggests that the N should count as a CCC for purposes of derating.
However I am not sure if a strict reading of the code would require this.
-Jon
Similarly if you have a wye source and an MWBC supplying loads which have different power factors, you could have a situation where N will carry as much current as the phases.
In these situations the physics suggests that the N should count as a CCC for purposes of derating.
However I am not sure if a strict reading of the code would require this.
-Jon