roger said:If you are refering to a two wire circuit, the grounded conductor is a current carrying conductor.
![]()
Roger
roger said:If you are refering to a two wire circuit, the grounded conductor is a current carrying conductor.
![]()
Roger
jwelectric said:If a load equal to the load on leg 1 was on leg 2 then we would have a "neutral" conductor would we not?
The definition is new for 2008 and IMO is not a true definition, although it has been common trade slang for a long time.Twoskinsoneman said:What do you mean "The conductor is not a neutral when only one leg is used"??
"Neutral Conductor. The conductor connected to the neutral point of a system that is intended to carry current under normal conditions."
roger said:The definition is new for 2008 and IMO is not a true definition, although it has been common trade slang for a long time.
Roger
Twoskinsoneman said:Ok... It's not slang anymore evidently. Just because it may not be a "true definition" in our opinions doesn't mean we shouldn't adapt to the NEC right?
The amazing thing about this forum is the honest search for what is really code... That is what is respected around here right?
roger said:See Mike's last post.
Now, let me ask you, as an engineer would you describe the grounded conductor of a two wire circuit as being a "neutral" conductor?
Roger
Twoskinsoneman said:Intresting... When I say "neutral" to my team of technicians they only hear "white wire"...
And that is the norm in the field as wellTwoskinsoneman said:Intresting... When I say "neutral" to my team of technicians they only hear "white wire"...
Which it is notTwoskinsoneman said:I completely understand where you are coming from though... I would not normally consider the grounded conductor of a two wire circuit as being a "neutral" conductor...
Yes in that it is part of a MWBC, and barring additive harmonics, would not add to the current flowing in the total number of circuit conductors.Twoskinsoneman said:Would you consider the CT conductor of a three wire circuit neutral if the circuit was severelly unbalanced?
Well, A neutral conductor carries only the unbalanced current from other conductors of the same circuit" is not perfect but works pretty good.What is your exact definition of a neutral wire?
roger said:And that is the norm in the field as well
Which it is not
Yes in that it is part of a MWBC, and barring additive harmonics, would not add to the current flowing in the total number of circuit conductors.
![]()
Well, A neutral conductor carries only the unbalanced current from other conductors of the same circuit" is not perfect but works pretty good.
Roger
jwelectric said:If a load equal to the load on leg 1 was on leg 2 then we would have a "neutral" conductor would we not?
Even worse, many people think every white wire must be a 'neutral.'Twoskinsoneman said:Intresting... When I say "neutral" to my team of technicians they only hear "white wire"...
Many years ago, I was taught that the grounded conductor was called the "identified" conductor, either by white or gray color, marking, ribbing, threads in the strands, etc.iaov said:Keeps it simpler for me although I will agree that the term "grounded conductor" may be more correct.
LarryFine said:Many years ago, I was taught that the grounded conductor was called the "identified" conductor, either by white or gray color, marking, ribbing, threads in the strands, etc.