neutral as current carrying conductor

Status
Not open for further replies.

tkirk911

Member
I have searched the web site and found various topics on this subject but none answered my question I have. Here goes. I have a 3 phase 4 wire wye system 120/208. If I take a 12/2 to feed convenience receptacles would I count the neutral? What if I ran 3 phase conductors (a,b,c) with 1 neutral sharing the neutral for convenience outlets would I count the neutral? I have read article 315 but am still confused. Help.
 
Re: neutral as current carrying conductor

For question 2 the neutral is not a current carrying conductor unless the major portion of the laod is nonlinear.
Don
 
Re: neutral as current carrying conductor

Hi Stew. You might be thinking of the EGC, which is, just as you said, included for fill but not not for ampacity adjustment. With the grounded conductor, it also is included for fill, but as far the ampacity adjustment goes...well, sometimes it is and sometimes it isn't. :)
 
Re: neutral as current carrying conductor

310.15(B)(4)(b) requires the neutral of a 4-wire "Y" system to be counted. And this is a "Y" system?
But is this question for race-way or box-fill count?
 
Re: neutral as current carrying conductor

Wayne,
The section you cite only requires the neutral of the 3 phase 4 wire system to be counted as a current carrying conductor when you are using 2 phases and the neutral. When you are using all 3 phases and the neutral, it is a current carrying conductor only when the major portion of the load in nonlinear.
Don
 
Re: neutral as current carrying conductor

tkirk911,

Here's the section of the NEC everyone is referencing. Hope it helps.

(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
 
Re: neutral as current carrying conductor

Whoops :eek: I was leaving out the two when I read it. As with out a load on the third phase there would only be three current caring conductors. Thank's Don sometimes I tend to read too fast. :D
 
Re: neutral as current carrying conductor

Originally posted by jeffhornsby:
You only count the neutral as a current carrying conductor if one the circuits is non-linear
Jeff, this is not true. Harmonics will accumulatively add on the neutral from all contributing phases. The harmonics would be out of phase with each other.

Roger
 
Re: neutral as current carrying conductor

Hi guys/gals
I am from Barbados where we use both IEE and NEC. My knowledge will tell me that a neutral is a live cable that has been earthed therefore cannot be counted as a current carrying conductor
 
Re: neutral as current carrying conductor

Bajan, a grounded conductor can carry the same current as the ungrounded conductor in a two wire circuit.

not_a_neutral.JPG


In a "Wye" configuration the grounded conductor can actually have more current flowing than any one ungrounded conductor in a multi wire circuit comprised of non-linear loads.

Roger

[ June 26, 2004, 11:47 AM: Message edited by: roger ]
 
Re: neutral as current carrying conductor

Roger i do agree with your illustration but the potential is different when dealing with the neutral. You will get a full potential when reading across a phase and a neutral or earth but between Neutral and earth there is an extremely small potential
 
Re: neutral as current carrying conductor

Originally posted by bajan:
Roger i do agree with your illustration but the potential is different when dealing with the neutral. You will get a full potential when reading across a phase and a neutral or earth but between Neutral and earth there is an extremely small potential
What does the potential between neutral and earth have to do with the neutral being counted as a current carrying conductor? :confused:
 
Re: neutral as current carrying conductor

Hello Bob, Bajan I must also ask, what does potential differences have to do with the heating associated with current flow in a grounded conductor?

Consider this, same potential and more current.

non_edison_circuit.JPG


The grounded conductor can be overloaded with no help from additional potential, the voltage is the same and has already dropped across the load/s but current must return to source.

Roger

[ June 26, 2004, 12:38 PM: Message edited by: roger ]
 
Re: neutral as current carrying conductor

Hey Bob
I will stand down on this issue because I understand something completely different from what you are referring to :cool:
 
Re: neutral as current carrying conductor

I really dont understand the discussions here. The situation presented in the sketch shows 20A flowing in a conductor but would nt the cable be already sized to allow the currents in the circuit and would the breaker control this flow .

What I got from the ? was if he had to count the neutral as a current carrying cable . If he already has his cables sized why would he consider it that way
 
Re: neutral as current carrying conductor

Originally posted by bajan:
I really dont understand the discussions here. The situation presented in the sketch shows 20A flowing in a conductor but would nt the cable be already sized to allow the currents in the circuit and would the breaker control this flow .
The size of the conductor and whether it is sized for the load is not the question here, it is the heating effect the current on the conductor will have inside of a conduit.

In a linear "multi-wire circuit" the grounded conductor does not add to the the heating effects in that it can theoretically be neutral, in otherwords, not have any current flowing at all.

true_neutral.JPG


Note: The illustrations are showing single phase and three phase Wye's are a little different, but in a 4 wire linear "multi-wire circuit" the same can apply.

Roger
 
Re: neutral as current carrying conductor



[ July 02, 2004, 01:31 AM: Message edited by: jes25 ]
 