Re: neutral as current carrying conductor
What is different about balanced, linear, three phase currents? What allows us not to count the neutral? The answer starts with the same discussion in my first paragraph. There will be a current leaving a load on Phase A, and it will travel along the neutral wire from the load to the point at which the ?shared neutral? splits off to form three separate neutrals (one associated with each phase). There will also be a current leaving a load on Phase B, and a third current leaving a load on Phase C. The three neutral currents will join at the split point, and from this point the net neutral current will flow back to the panel. But if you add the three currents (recall they are not in phase with each other), and if the load is balanced, and if there are no significant harmonics, then the sum of the three neutral currents will be zero. No neutral current will flow back to the panel. Instead,
</font>
True. From that fact we may infer that there is no current between the neutral conductor and planet Earth. However, there is a potential difference between the (let us call it) ?neutral side of the load device? and the (let us call it) ?neutral point of the panel.? This potential difference will cause a current to flow from the load to the panel (and from there, ultimately, back to the source) along the neutral conductor. Therefore, we count the neutral as a current-carrying conductor.Originally posted by bajan: . . . between Neutral and earth there is an extremely small potential
What is different about balanced, linear, three phase currents? What allows us not to count the neutral? The answer starts with the same discussion in my first paragraph. There will be a current leaving a load on Phase A, and it will travel along the neutral wire from the load to the point at which the ?shared neutral? splits off to form three separate neutrals (one associated with each phase). There will also be a current leaving a load on Phase B, and a third current leaving a load on Phase C. The three neutral currents will join at the split point, and from this point the net neutral current will flow back to the panel. But if you add the three currents (recall they are not in phase with each other), and if the load is balanced, and if there are no significant harmonics, then the sum of the three neutral currents will be zero. No neutral current will flow back to the panel. Instead,
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The Phase A neutral current flows into the Phase B and Phase C loads</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The Phase B neutral current flows into the Phase A and Phase C loads, and</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The Phase C neutral current flows into the Phase A and Phase B loads.</font>