Grounded, GEC EGC, SBJ are (should be) all bonded at one location, in one enclosure. From what your earlier posts states, it is properly "bonded". Bonded is in quotation marks because loose connections rescind the "properly"you would be correct. the transformer is properley grounded to the main grounding conductor as well as building steel. the neutral is created in the transformer as its delta/wye. you wouldnt bond them there would you?
... the main disconnect for the entire building itself has the neutral and ground bonded. my subpanel does not have them bonded...
Can you recreate the scenario now, since you have energized everything? Did you check for voltage on the circuits when this happened, or did you just assume there was no voltage because the breakers were in the off/tripped position? I'm asking because on very [very, very] rare occasions a breaker (even a new one) will "temporarily" be defective.