Neutral Bar

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
I need to add some circuits to this old Square D QO panel. The neutral bar is already pretty full with a lot of neutrals doubled up. Should I just add a ground bar and move some of the grounds to the new ground bar?

IMG_2733.jpeg
 
Never understood why a panel was not required to come with as many ground and neutral screws as the panel maximum configuration allows.
What configuration, all 2 pole MWBC? How about all 1 pole branches with EMT used as the ground?
 
Never liked the panels (Murray was one) with 1 NB behind the other. The back bar is harder to see so most fill the front bar first. Then when the front bar is full its really hard to see in the back
 
Where's the MBJ?
I was wondering about that. I was wondering if it was missing the green screw to the neutral. That’s what you’re referring to, correct?
Did old Square D QO panels use a green screw, or was it some other method?
 
Take all your #14 and #12 grounds off, twist a bunch of them together and pigtail each bunch with a big wire nut or split bolt to the ground/ neutral bar with a single #12. Keep going until you've done all your grounds. Don't leave it that way. That should free up probably half the spots.

-Hal
 
I was wondering about that. I was wondering if it was missing the green screw to the neutral. That’s what you’re referring to, correct?
Did old Square D QO panels use a green screw, or was it some other method?
Correct.
 
Take all your #14 and #12 grounds off, twist a bunch of them together and pigtail each bunch with a big wire nut or split bolt to the ground/ neutral bar with a single #12. Keep going until you've done all your grounds. Don't leave it that way. That should free up probably half the spots.

-Hal
You said “Don’t leave it that way”, what do you mean?
 
How would you even add a ground bar in that mess? I would disconnect everything on the neutral bar and start over. Once that mess is out of the way you could add a ground bar.
 