This is my first time installing a transformer of this type. I know I have to bond my XO in your most common 480 delta stepped down to 120/208 wye but not sure about if I have to bond what is the X3 (or X4, they’re connected) terminal which is where my neutral is landing. Again, this is a 480 SINGLE phase primary stepping down to SINGLE phase 120/240. Please help! Thanks!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
240/120 systems need to be grounded (250.21) and bonded (250.30) normally with a X2-X3 bonding jumper. (see 250.30 for exceptions )
 

Sparky480V

Member
Location
Sacramento Ca
Thanks!

Thanks!

Thanks for the fast answer! I’ve attached pertinent photos even though you answered my question. All I have to do is go from the X3(X4) lug to the bond and it’s all good.

... except for the noalox and torquing of the secondary wires. They’re in there for the sake of the photo and will be taken out before I heat up the transformer and test the secondary voltage.

Again, thank you!
 

Attachments

  • B704DC4C-2147-4380-94E3-AACDF7011710.jpg
    B704DC4C-2147-4380-94E3-AACDF7011710.jpg
    18.3 KB · Views: 52
  • 3D808D2F-28F9-40BF-8CFE-B1F027717977.jpg
    3D808D2F-28F9-40BF-8CFE-B1F027717977.jpg
    22.2 KB · Views: 61

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Thanks for the fast answer! I’ve attached pertinent photos even though you answered my question. All I have to do is go from the X3(X4) lug to the bond and it’s all good.

... except for the noalox and torquing of the secondary wires. They’re in there for the sake of the photo and will be taken out before I heat up the transformer and test the secondary voltage.

Again, thank you!

Yes a system bonding jumper and a grounding electrode conductor to your grounding terminal
If you are under '17, see 450.10(A)..
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Thanks for the fast answer! I’ve attached pertinent photos even though you answered my question. All I have to do is go from the X3(X4) lug to the bond and it’s all good.

... except for the noalox and torquing of the secondary wires. They’re in there for the sake of the photo and will be taken out before I heat up the transformer and test the secondary voltage.

Again, thank you!

Just to be clear, X1 will be line 1, X4 will be line 2. X2 and X3 tie together and bond. As Augie mentioned, your going to need a grounding electrode as well.
 

Sparky480V

Member
Location
Sacramento Ca
Detailed photo

Detailed photo

Just to be clear, X1 will be line 1, X4 will be line 2. X2 and X3 tie together and bond. As Augie mentioned, your going to need a grounding electrode as well.

Thanks for the input. I have it as you explained. Attached is a photo with markups detailing the installation.
 

Attachments

  • CF32CF10-8DDD-4B10-BF7C-3BF29C7C9E61.jpg
    CF32CF10-8DDD-4B10-BF7C-3BF29C7C9E61.jpg
    22.8 KB · Views: 61

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What size are your secondary conductors and the GEC/SSBJ? The green conductor run with the secondary is the SSBJ (supply side bonding jumper).

Here's a similar transformer with a straight 240 volt secondary. Sorry it's a bit blurry.

IMG_20160831_130113.jpg
 