I have a 2mw PV system that has 46 inverters feeding 9 power panelboards to a switchgear to a padmount transformer to 13.8kv into a powerhouse of a manufacturing plant in MA.
The inverters generate 480/277v 4w. The 4w is brought through the whole system to the main switchgear.
The engineer has designed use of 277v to feed power supplies for the monitoring off of the inverters at the panelboards.
Do the neutrals get bonded at the panelboards that are fed from the inverters (9 connections), or at the main switchgear at the transformer?
We have a 3/0 ground loop throughout the system.
Also the engineer has designed a transformer the has a 480/277v 4w wye primary and a 13.8kv delta secondary.
He is showing the neutral from the PV system connected at the transformer.
Should the neutral be connected at the transformer?
Whenever we used a transformer in this configuration, it has always been understood to not connect the neutral to a wye primary.
The inverters generate 480/277v 4w. The 4w is brought through the whole system to the main switchgear.
The engineer has designed use of 277v to feed power supplies for the monitoring off of the inverters at the panelboards.
Do the neutrals get bonded at the panelboards that are fed from the inverters (9 connections), or at the main switchgear at the transformer?
We have a 3/0 ground loop throughout the system.
Also the engineer has designed a transformer the has a 480/277v 4w wye primary and a 13.8kv delta secondary.
He is showing the neutral from the PV system connected at the transformer.
Should the neutral be connected at the transformer?
Whenever we used a transformer in this configuration, it has always been understood to not connect the neutral to a wye primary.