Infinity is saying no, but I am saying yes. I look at it like this... The rules for separately derived systems, in most cases parallel the rules for services. Large facilities, like the UF campus here have customer owned utilities. Those are not services, even though the entire campus distribution system is identical to a utility. The University is not a utility. That code cited, doesn't state that a transformer can only feed one system, so each system can have its own bond.If they run neutral to fire pump controller disconnect can I put neutral to ground bond in it fire pump controller? I would now have two secondary disconnects and one of them SWBD has neutral to ground bond.
Please see attached what I have. NEC 2017 Article 250.30(A)(1) says system bonding jumper can be at any single point on the separately derived system from the source to the first system disconnecting means.
Do I have first system disconnecting means in the attachment this post?
View attachment 2581179