If I install 3, 20 amp 1 phase branch circuits (12 AWG), can I use 1 common neutral conductor (12 AWG)?
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The panel label is not really relevant, you need to know what the supply system is. Is it single phase, three phase, four wire wye, four wire delta, etc...?

Roger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Butler,
The system is a 120/240 volt, 3 phase, 4 wire wye
There is no such system. If it is a a wye, the voltage is 208, not 240. If you have 240, then it would be a 4 wire high leg delta.
Don
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Butler said:
You are correct it is 208. Can you help me with the neutral question?
Now we can.

Yes, as long as no two line conductors originate from the same phase.

Keep in mind that was a very general question, as is the answer.
 