Neutral Calculation

Status
Not open for further replies.

Butler

Member
If I install 3, 20 amp 1 phase branch circuits (12 AWG), can I use 1 common neutral conductor (12 AWG)?
 
Last edited:
The panel label is not really relevant, you need to know what the supply system is. Is it single phase, three phase, four wire wye, four wire delta, etc...?

Roger
 
Butler,
The system is a 120/240 volt, 3 phase, 4 wire wye
There is no such system. If it is a a wye, the voltage is 208, not 240. If you have 240, then it would be a 4 wire high leg delta.
Don
 
Butler said:
You are correct it is 208. Can you help me with the neutral question?
Now we can.

Yes, as long as no two line conductors originate from the same phase.

Keep in mind that was a very general question, as is the answer.
 