If you had a 3 phase load with no neutral as you mention above then you don't need to pull a neutral at all. If you had a panel with rtu and other loads then you would use T. 250.122 for the lowest possible conductor for the neutral. It cannot be smaller then the egc.
I assume you are talking about a feeder panel here. If it is/were a service panel, the minimum size is per 250.66, and a neutral is required to be pulled to the service disconnecting means.
 
I assume you are talking about a feeder panel here. If it is/were a service panel, the minimum size is per 250.66, and a neutral is required to be pulled to the service disconnecting means.


This is a tenant taking up a empty space in a shell building
 
I assume you are talking about a feeder panel here. If it is/were a service panel, the minimum size is per 250.66, and a neutral is required to be pulled to the service disconnecting means.
That is correct as we have already mentioned 3 or 4 times already in this thread that the service gets the GEC and the feeder gets the egc.:)
 
That is correct as we have already mentioned 3 or 4 times already in this thread that the service gets the GEC and the feeder gets the egc.:)
...and out of those 3 or 4 times, 2 of 'em are mine :D

Np has not confirmed which and your post gave only a feeder panel conclusion. Until confirmed as one or the other, I feel both service and feeder panel conclusions need to be addressed in any response.
 
...and out of those 3 or 4 times, 2 of 'em are mine :D

Np has not confirmed which and your post gave only a feeder panel conclusion. Until confirmed as one or the other, I feel both service and feeder panel conclusions need to be addressed in any response.

Well -- go ahead-- enjoy yourself. :)

Actually I thought he , sort of , confirmed it with this post.

Npstewart said:
OK for the service neutral I would use 250.66?
 
Well -- go ahead-- enjoy yourself. :)

Actually I thought he , sort of , confirmed it with this post.
I feel much better now that I have your permission ;)

I sort of thought so too... and that was post #15. You responded with post #16, while the post of yours I commented on is #18.
 