I don't understand your question. I would think the neutral calculation already includes "load diversity."
The point is if I have a calculated load on a service of 100amps I could use all #4 service conductors however, if the calculated load for the service is larger than 100 amps but the calculated load for the neutral is 100 amps then I cannot use T. 310.15(B)(7) even though it is the same calculated load as the service above.
Here is why-- If the calculated load for a dwelling is 100 amps the chances are pretty good that the neutral conductor will not see 100 amps or anywhere close to it. If the neutral calculated load is 100 amps then that means there is a better chance that the neutral will see 100 amps although I doubt, in reality, it ever will be close.