neutral conductor

Status
Not open for further replies.

fnluk

Member
For table 310.15b2a-#4 neutral conductor does that mean if you pull a seperate neutral for each ungrounded conductor you do not count the neutral for derating purposes
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: neutral conductor

If you pull a grounded conductor for each ungrounded conductor you will not have a neutral at all, and all the conductors will be current carrying conductors, so they will all be counted for derating.

Roger
 