Neutral conductors in 3 way lighting circuits

Merry Christmas

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I will add that you can skip the neutral in one location in a 3-way circuit if the other box is on the same level and the entire lighted area is visible from each location. Without pulling up the article, believe that is the way it is worded.
 

VirutalElectrician

Senior Member
Location
Mpls, MN
Occupation
Sparky - Trying to be retired
I've got a scenario that I have been explaining to people and would like to know the code reference:

-There is a 15A 120V lighting circuit that enters box "A" which is a 2g switch box with (2) 3way switches. There are (2) 14/3 romex going to box "B" which is a 2g switch box with (2) 3 way switches. Leaving box "B" are (2) 14/2 switch legs going to separate lights.
I utterly hate this configuration. When working with smart homes and smart switches, the line and load should be entering and leaving the same box.
 