Neutral Current and Heat Generation

Thank you everyone for your inputs so far. We have gotten information back from the vendor on the transformer resistance and the neutral current is not contributing to any significant heat rejection.

That being said we do have around 10.5% THD. I dont have individual values for each harmonic level, but is there a calculation out there that can be used to calculate heat dissipation from harmonics?
 
Ok i get that, and again, i am not concerned with the temperature of the Transformer. Looking to see if heat rejection due to harmonics can be calculated.
 
Ok i get that, and again, i am not concerned with the temperature of the Transformer. Looking to see if heat rejection due to harmonics can be calculated.
As Ron mentions in post #21, this is an issue which K rated transformer were marketed to accommodate, do some research on these.
It has been some 20years since I amazed whether a K-1 versus a K-13 transformer was needed. I recall looking at some DOE and IEEE literature on this subject. After all the analysis we stayed with a standard K-1 unit.
 
I've been researching online about this and found a few articles about how to calculate this.

This shows how to calculate K-factor by making a table based on all the harmonic values. I have done this on my end, and K-factor is less than 1. Can anyone see anything that i did wrong here?1736519876817.png

Second one i found was to calculate power factor based on harmonics.
I have also done this one on my end. And found ~0.997 PF thd. Is there a way that i am not calculating the Neutral THD into this?
1736520149745.png
 
I've been researching online about this and found a few articles about how to calculate this.

This shows how to calculate K-factor by making a table based on all the harmonic values. I have done this on my end, and K-factor is less than 1. Can anyone see anything that i did wrong here?View attachment 2575120

Second one i found was to calculate power factor based on harmonics.
I have also done this one on my end. And found ~0.997 PF thd. Is there a way that i am not calculating the Neutral THD into this?
View attachment 2575121
That is a lot less triplen harmonic (3, 9, 15) than I would have expected with so much neutral current.
Clearly you have a lot of 6 pulse VFDs with high 5th and 7th.
FWIW, I've never calculated K-factor so I can't help with that.
 
That is a lot less triplen harmonic (3, 9, 15) than I would have expected with so much neutral current.
Clearly you have a lot of 6 pulse VFDs with high 5th and 7th.
FWIW, I've never calculated K-factor so I can't help with that.
The reading taken with the 397% THD on Neutral was taken on the 415V Transformer (PDU). The breakdown calculation of each harmonic level was taken at the upstream Medium Voltage transformer, since the meter on that is much more accurate to break down the individual harmonic levels.

Im trying to get a reading taken on the 415V transformer so i can see the individual harmonic levels, but i just really wanted to see if im doing these calculations correctly.

K-Factor calc was done on Medium Voltage transformer.

PF-thd calc was done using the reading on the 415V transformer.
 
This shows how to calculate K-factor by making a table based on all the harmonic values. I have done this on my end, and K-factor is less than 1
This does not surprise me at all.
The need for K-Rated transformer is extremely exaggerated. But, it is a good idea to check if your application is an outlier.
 