I concur :smile:crossman said:...since the service neutral has to be sized based on the maximum unbalanced load, we're okay.
I concur :smile:crossman said:...since the service neutral has to be sized based on the maximum unbalanced load, we're okay.
crossman said:Back to the original thought of the OP:
After having pondered this a good bit more, I still hold the conclusion that, considering normal residential loads, there is no way to overload a properly sized service neutral conductor regardless of the loading. There just aren't any scenarios where the service neutral carries more current than the unbalanced load.
And since the service neutral has to be sized based on the maximum unbalanced load, we're okay.
tallgirl said:which section explicitly states that the neutral conductor in a grid-interactive solar power system must be sized to carry the sum of the greatest LOAD and greatest SUPPLY.
gar said:080712-2149 EST
crossman:
I am not sure how your comment on code compliant fits into the description I provided.
From hot line 1 to neutral I have a load that draws current from 80 to 85 degrees with a peak value of I1. Assume it to be a rectangular pulse. This dissipates I1^2*Rneutral*5/360 watts.
From hot line 2 to neutral I create an identical pulse but delayed to occur between 95 to 100 degrees and of opposite polarity. Clearly these do not overlap and therefore do not cancel. This second pulse dissipates the same power in the neutral as the first pulse.
Thus, if we assume the neutral wire size is the same as either hot line, then the power dissipated in the neutral is double that in either hot line. Note: power dissipation has nothing to do with the polarity of the current when the different currents do not overlap.
This is something I could create. Why? I have no idea for a use other than to prove that in a center tapped single phase application that I can produce a higher neutral current than the current in either hot line.
iwire said:240.4 :wink:
tallgirl said:I disagree. Were does it say how to calculate the maximum neutral current?
iwire said:I know as well as you do that it does not say that.
But it does require us to protect conductors at or below their ampacity, how that is accomplished is largely irrelevant to that section.
tallgirl said:Are you using the 2008 NEC? I think mine is at the office, and it being Sunday I don't want to have to go to the office.
The 2005 NEC has over temperature protection for 310.10. Or am I under caffeinated?
JohnJ0906 said:
220.61 Feeder or Service Neutral Loadtallgirl said:W[h]ere does it say how to calculate the maximum neutral current?
tallgirl said:But it's still the section on temperature limitations of conductors
If both hot lines and the neutral are the same material and wire size, then the resistance of each of those wires is the same, and the temperature ratings will be the same. If the hot lines are sized for their load RMS current, then the power dissipation in one of those lines is = I^2*R.And so what if the power in N is twice L1 or L2 -- that's irrelevant to the current in N and it's relationship to the maximum ampacity N was sized to carry.
I have no idea what this paragraph means. I created an example with a single pulse in each hot line, each with the same value of RMS current, and the pulses were non-overlapping. Thus, the composite current in the neutral consists of two pulses, and this of necessity increases the RMS current in the neutral.I disagree with your assertion that the current would be higher, especially since you stipulated that they do not overlap. If there is no overlap, L1 = N or L2 = N. There's never a situation, because there is no overlap, where N = L1 + N.
This example creates a full-wave center tapped rectifier with a full wave rectified current in the neutral.Here's a much easier scenario -- you have a half-wave rectifier between L1 and N, and between L2 and N. The outputs of both rectifiers are driving 180 degree loads at maximum rated capacity during each legs' positive cycle. What is the LOAD on N? Not the load on N relative to L1 and L2, what is the actual value of the load on N?
tallgirl said:Ah, but now you're starting to get into the domain of the real problem. The service neutral is sized for the maximum unbalanced LOAD, per 220.61. There is no discussion in here about anything but LOAD and the problem isn't LOAD
gar said:crossman:
I answered you question of peakiness above. I am basing the analysis on RMS current. The only reason for the narrow peak was to provide an easy illustration that would separate the two components.
The full wave rectified example above does the same thing with less peaking.
crossman said:Here are my thoughts on current directions. This, of course, is for one half of the sine wave, for the other half, just reverse all the arrows.
The black leg from the utility is 5 amps SELL and the red wire from the utility is 5 amps BUY.
ELA said:I do not understand this concept of 5 amps sell and 5 amps buy? Wouldn't it really be that the primary of the transformer would just see a lessor demand by the amount of the load that the inverter was taking up? We do not really have two independent sources from the utility do we?
ELA said:I was having a hard time with the diagram since it shows a total load of 2400watts load and the inverter providing 2400 watts load power. This would imply a net of zero from the utility ?
ELA said:I know little about dual leg inverters, do they really have to supply equal currents on both legs?
ELA said:I would think the inverter legs would supply a variable current on each leg as required up to a current limit point. At that point the utility would then take over.