Jsim4109
- Cherry Hill, NJ,USA
I have an installation for a solar field connected to a high school. The school utility service is 120/208v grounded wye. The solar field is a line side tap before the main service disconnect. The solar tap conductors first go to a 1200A disconnect switch. After the switch is a transformer. The transformer nameplate is 1000kva 5.86%Z, HV 480v, LV 208GrndY/120. The conductors leave the transformer to the solar inverters at 480v. During troubleshooting, we discover that there is 154A on the neutral between the line side tap and the transformer. We shut the inverters off and the currents are still there. We installed the meter between the disconnect and the transformer and the currents are there. It would appear that the neutral currents are coming from the school service. But when we open the disconnect to the transformer, the neutral currents go away. Any thoughts?