Neutral Currents
jmd445
In a strictly resistive 208v 3 phase circuit :
Ia=8 amps, Ib=10 amps and Ic=15 amps, how would you calculate the neutral impalance (current on the neutral)
How about a non-linear circuit?
Thanks,
Jim
I don't think we are talking about a single, three-phase load, such as a single motor, but rather a group of loads that yield that particular set of currents.
In = Square Root of {Ia*Ia + Ib*Ib + Ic*Ic - Ia*Ib - Ia*Ic - Ib*Ic}
While the formula Charlie has provided will give you the correct answer, simply figuring the greatest imbalance between any two legs is usually sufficient. So in the case of your particular numbers, the load would be roughly 7A on the neutral. If you perform the above calculation, you will be very near to that value, around 6.2A or so.
Charles and Brian, thank you. Jim
Barbeer, what makes you think I don't have a neutral, suppose the circuit I described were three heating elements in a press that were phase to neutral as opposed to line to line?
Because you said 208 which, usually is 3 phase 3 wire, 3 phase 4 wire is stated as 208/120, what gave away that you might mean with a neutral/grounded conductor is the current imbalance, though you could have single phase 208 loads.
Jim,
The answer changes if you have line-line rather than line-neutral loading.
If you assume line-neutral _resistive_ loading, than Charlie's answer is the correct one.
If you assume only line-line _resistive_ loading, then your numbers are not possible.
If you assume a mixture of both line-line and line-neutral resistive loading, then the neutral current could be as low as 2.89A.
The detailed way to solve these sort of problems is to represent your currents as vectors, and then to add them up.
-Jon
Yes, perhaps my wording was a little bland.............since the heading was neutral currents and 208 volts was in the body of the post, I was assuming it would be read as 208/120 (fatal error on my part).
As for the vector theory, I found an interesting website
http://www.electrician2.com/electa1/electa3htm.htm
This explains it in rather technical matematical terms.
I was hoping for a simple matematical formula that would put this in layman's terms.
Jim
The mathematical formulas are necessarily complex; if you want to get this in layman's terms, IMHO you are better off thinking in terms of pictures.
Remember that we are talking about alternating current. This means that the current measured at a point is a continuously varying value. We _identify_ this continuously varying value with a continuously varying mathematical function, the _sine_ function. The benefit here is that a sine function can be described by only a few numbers: amplitude, frequency, and phase angle.
Similarly the current in each of the phases can be identified with suitable sine functions, and described with a very few parameters.
Generally, we accept that there is only a single frequency in the system (60Hz in North America), so don't bother reporting it.
Additionally, we generally report the RMS voltage or current, rather than the _peak_ voltage or current, though mathematically the _amplitude_ of the sine wave is the peak value. This doesn't matter for the present discussion.
If you simply accept the following as truth (it can be shown mathematically, but the proof is not relevant at the moment): given a set of sine functions, all of the _same_ frequency, but of arbitrary amplitude and arbitrary phase relationship, you can _represent_ each of these sine functions as a _vector_. The amplitude of the sine function is represented by the _magnitude_ (length) of the vector. The relative phase angle of the sine function is represented by the _direction_ (angle) of the vector.
In other words, in the world of our simplifying assumptions, we can _represent_ the values that we are dealing with as line segments with length and direction. The great thing here is that it lets us deal with several rather complex problems in a _graphical_ fashion, one that we can see and intuit quite easily.
For example, consider the neutral current question that we are asking here. By the 'kirchhoff current law' the net current flowing into a 'node' must be zero. This means that the current flowing down the neutral wire from the common point must exactly equal the net current flowing into the common point from the loads, so that the _net_ current flowing into the common point is zero. So we have to answer the question "What is the sum of Ia + Ib + Ic?"
The problem, of course, is that Ia, Ib, and Ic all have different phase angles. So we can't simply add the current magnitudes up; there is some sort of canceling going on here.
But if we say that Ia is represented by a vector of length 8, and direction 0 degrees, Ib with length 10 and direction 120 degrees, and Ic with length 15 and direction 240 degrees, and we use the rules of vector addition to add these up, we get that the net current flowing into the neutral from the loads will be represented by a vector of length 6.24 and angle of 224 degrees. The _graphical_ representation of a vector is simply a line segment with length and direction, and the graphical representation of vector addition is simply placing these line segments 'head to tail'.
-Jon
...because there is no neutral with line-to-line loads.
The numbers are possible. An imbalance in loading changes the line currents' angle (i.e. vector direction) such that they are not at 0?, 120?, and 240?. Instead, they would be...
Ia = 8A @ 25.784?
Ib = 10A @ 93.372?
Ic = 15A @ 243.831?​
The loads currents would be...
Iab = 0.679A @ 330?/150?
Ibc = 9.643A @ 90?/270?
Ica = 7.638A @ 210?/30?​
Whoops, Smart $ I missed that.
You are quite correct.
When I was going over the problem in my head, I mistakenly constrained the result to having a 120 degree phase difference.
-Jon