The motor is rated 120/240. It is at the end of a 1500' run. I am concerned about the voltage drop on the motor.
Yea, even at 240 that's going to be an issue. Did you consider a step up then step down transformer?
You know, that could really help the situation. Convert the 208 to 480 (or 600?) then back down to 120/240 at the end of the pier?