Does it mean you can feed a nonlinear load with a common grounded wire?!!!:?OP never stated type of loads and the NEC would not require it regardless.
Does it mean you can feed a nonlinear load with a common grounded wire?!!!:?OP never stated type of loads and the NEC would not require it regardless.
Does it mean you can feed a nonlinear load with a common grounded wire?!!!:?
Yes, and it is a very common instatallion. In some cases the common grounded conductor is larger than the phase conductors, but not always.Does it mean you can feed a nonlinear load with a common grounded wire?!!!:?
Yes, and it is a very common instatallion. In some cases the common grounded conductor is larger than the phase conductors, but not always.
Specs that were influenced by the Copper Development AssociationI get specs for a #10 neutral to the first break off junction point on a 20A MWBC for fluorescent lights, computers, and such a lot.
Specs that were influenced by the Copper Development Association
Do you pay attention to that? I know for some places, for example hazzerdious locations or pools, you may need it. But when you get a store or residential work and the architect states "EMT with grounding conductor" do you put it in, or let the EMT be the ground?
Thanks
Mike
If the design calls for the EGC, then you provide and install it.Do you pay attention to that? I know for some places, for example hazzerdious locations or pools, you may need it. But when you get a store or residential work and the architect states "EMT with grounding conductor" do you put it in, or let the EMT be the ground?
Thanks
Mike
Does it mean you can feed a nonlinear load with a common grounded wire?!!!:?