Does 404.2(C) require a neutral for a switch controlling a half hot for a plug-in table lamp (assuming that the exceptions do not apply for a given installation)?
The textbook says "yes", and I have said "yes" in the past, since 404.2(C) does not reference "luminaires", but "lighting loads." 210.70 permits switched receptacles in lieu of luminaires. That indicates the switched receptacles are for lighting loads.
However, 404.14 still (rightfully) forbids dimmer switches from being installed to control receptacles.
My main bone to pick with this is that the textbook shows a 14-4 NM being used as travelers between a set of threeways in a bedroom, in order to carry a full-time hot along for the ride. There is also a ceiling fan with light kit shown in the room, so these switched receptacles are not "code-required switched receptacles in lieu of lighting outlets", they are simply switched receptacles.
Bearing in mind I am teaching first years here, I am inclined to recant my earlier grumblings about the use of 14-4 wire in the text and say that the 14-4 is required. I have already made it clear that a neutral is not required for other loads, such as disposals and so on.
What would you do?
The textbook says "yes", and I have said "yes" in the past, since 404.2(C) does not reference "luminaires", but "lighting loads." 210.70 permits switched receptacles in lieu of luminaires. That indicates the switched receptacles are for lighting loads.
However, 404.14 still (rightfully) forbids dimmer switches from being installed to control receptacles.
My main bone to pick with this is that the textbook shows a 14-4 NM being used as travelers between a set of threeways in a bedroom, in order to carry a full-time hot along for the ride. There is also a ceiling fan with light kit shown in the room, so these switched receptacles are not "code-required switched receptacles in lieu of lighting outlets", they are simply switched receptacles.
Bearing in mind I am teaching first years here, I am inclined to recant my earlier grumblings about the use of 14-4 wire in the text and say that the 14-4 is required. I have already made it clear that a neutral is not required for other loads, such as disposals and so on.
What would you do?