I present for your consideration and input:
Customer states that lights throughout the residence are flickering/dimming and that small kitchen appliances are not functioning correctly.
I arrive, check voltages A to B, A to N, B to N & A/B to G at the utility pole. Everything checks out and all connections are tight. Underground feed is approx 120' to the residence.
At the panel all connections are tight at the main breaker, neutral bar, ground bar, branch circuit breakers and bussing.
Kitchen has 2- 20 amp small appliance circuits. I power up the microwave and check voltage on the circuit; voltage drops to 90 volts after 1 second of the micro running. Voltage returns to 120 when micro shuts off. Same issue on the other appliance circuit when the air fryer is turned on; voltage drops to 90 until air fryer is turned off. This anomaly is seen at the breaker AND the line side of the main breaker BUT NOT at the utility pole. The other odd part is that when voltage drops to 90 on A phase the voltage increases to 140+ on B phase and viceversa. (The neutral is not floating in the panel but that shouldn't cause this type of issue now)
HO has been at residence for 5 years, no work has been done on the kitchen circuitry and this issue just started last week.
My thoughts are that the neutral/grounded conductor between the utility pole and the panel has been compromised......or am I missing something???
I am interested to hear if any of you have encountered this and what possible solutions there might be.
TIA
Customer states that lights throughout the residence are flickering/dimming and that small kitchen appliances are not functioning correctly.
I arrive, check voltages A to B, A to N, B to N & A/B to G at the utility pole. Everything checks out and all connections are tight. Underground feed is approx 120' to the residence.
At the panel all connections are tight at the main breaker, neutral bar, ground bar, branch circuit breakers and bussing.
Kitchen has 2- 20 amp small appliance circuits. I power up the microwave and check voltage on the circuit; voltage drops to 90 volts after 1 second of the micro running. Voltage returns to 120 when micro shuts off. Same issue on the other appliance circuit when the air fryer is turned on; voltage drops to 90 until air fryer is turned off. This anomaly is seen at the breaker AND the line side of the main breaker BUT NOT at the utility pole. The other odd part is that when voltage drops to 90 on A phase the voltage increases to 140+ on B phase and viceversa. (The neutral is not floating in the panel but that shouldn't cause this type of issue now)
HO has been at residence for 5 years, no work has been done on the kitchen circuitry and this issue just started last week.
My thoughts are that the neutral/grounded conductor between the utility pole and the panel has been compromised......or am I missing something???
I am interested to hear if any of you have encountered this and what possible solutions there might be.
TIA