I’m getting mixed reviews. Is the ground lug kit TGL20CP recommended for use as a neutral lug? Or is it egc only.
Totally....I wonder sometimes if stuff like this has more to do with "we didn't bother to do the legwork, which is often just paperwork, to get this UL".It baffles me why they can't design a lug that can be listed for both the EGC and a neutral. Better yet that should be required by the listing of the lug.
I agree. the one aftermarket lug that is neutral rated for GE that attaches to the rail seems to be much harder to find.It baffles me why they can't design a lug that can be listed for both the EGC and a neutral. Better yet that should be required by the listing of the lug.
I think the answer may be this. A ground lug only has to sustain current flow for a few cycles until the OCPD opens up. The neutral lug has to sustain full load indefinitely.Does a lug need a different listing depending on what color wire comes into it? I would think that if the lug is rated for the connection methods at both ends (lug to wire, lug to case or whatever), it doesn't matter where it's an EGC or a neutral. (Of course an isolated neutral bar would need the proper standoffs/insulation, but say in a service disconnect.)
Cheers, Wayne
Thanks, that is a plausible distinction, so the next question is whether the listing standards do in fact reflect that distinction, and have different tests for the two types of lugs. And whether the grounding lug test standard is, in fact, less rigorous than the neutral lug testing standard.I think the answer may be this. A ground lug only has to sustain current flow for a few cycles until the OCPD opens up. The neutral lug has to sustain full load indefinitely.
Try UL 467 for grounding connections and 486A, B and C for other connectors.Thanks, that is a plausible distinction, so the next question is whether the listing standards do in fact reflect that distinction, and have different tests for the two types of lugs. And whether the grounding lug test standard is, in fact, less rigorous than the neutral lug testing standard.
If someone points me to the correct UL standard to page through, I'm happy to at least cursorily investigate.
Cheers, Wayne
UL 486A-B is spot on for a neutral bar, section 1.1(e) of the Scope is "neutral bars".Try UL 467 for grounding connections and 486A, B and C for other connectors.
And that higher short time current for grounding connections was the reason Ideal tried to insist that the only wire nut that could be used for rounding was their Greenie. That insistence resulted in 250.8 including any listed pressure connector as a permitted termination method for grounding....
So as suggested, the difference comes down UL 467 having a "short time current" test with a larger current, and UL486A-B having a "current-cycling test."
But it sounds like if you have a product labeled as "ground bar," if it is listed to UL 486A-B, you can use it as a neutral bar; if not, you can't?
Cheers, Wayne
How does a grounding connection have a higher current than the line conductor?And that higher short time current for grounding connections was the reason Ideal tried to insist that the only wire nut that could be used for rounding was their Greenie. That insistence resulted in 250.8 including any listed pressure connector as a permitted termination method for grounding.
I think that it's more that the grounding connections (UL 467) are tested for fault conditions, as that's the main stressor on them. Whereas as the normally current carrying connections (UL 486A-B) are tested for temperature behavior from current cycling, and not explicitly tested for fault conditions.How does a grounding connection have a higher current than the line conductor?
It was Ideal's assertion that it would not, but of course they wanted to sell more green wirenuts.I think that it's more that the grounding connections (UL 467) are tested for fault conditions, as that's the main stressor on them. Whereas as the normally current carrying connections (UL 486A-B) are tested for temperature behavior from current cycling, and not explicitly tested for fault conditions.
Perhaps the assumption is that if it passes the current cycling test, it would pass the short-time current test?
Cheers, Wayne