I would tend to concur. But if it was important enough to not run new wire And I was going to use it as an egc then I would feel a little better about it after slappin' a megger on it.
I just did 3 of these in a domitory. They had 2 blacks and a green in the conduit and when they got new machines they just slapped the green on the neutral terminal and left the grounding strap on. Well, they had the old surface mount 3 prong receptacle and the neutral got smushed when replugging it in and didn't connect as it should. So the residence were coming down to the concrete laundry room floor barefooted and getting hammered when they turned on that machine and touched it.
fortunately I did have 1" conduit, plenty of wire, and plenty of time and only about 25 feet to go. I ended up just changing all 3 on that floor with new recep's, plug cords, and pulling the jumpers off of the equipment. I realize that not everyone has this luxury though and just hope the OP makes it a safe installation.
Megging the AC sheath will not tell you anything about how much impedance it will have when carrying a heavy current from a ground fault.
A megger is for testing insulation integrity and not for measuring low resistances.
I also think you would have had people getting shocked on the concrete floor even if some other wiring method was used - use of the neutral for equipment grounding was the problem here, and I have seen this before on code compliant (3 wire) installs of ranges or dryers that have grounded surfaces nearby. Just one more reason why they eventually decided we need 4 wires to these appliances instead of 3.