Greetings group
For a 4 wire lighting circuit powering a HID lighting load, that uses hi frequency ballasts, do any of you up-size the neural for harmonics?
Circuit size is 20Amp 4 wire 480/277. Load is about 9500 VA and with the continuous factor ~11875 VA (or ~15A)
Here is an example ballast:
EDIT: I should add the balasts are all 277V L-N loads
Also late to this party, but I believe 210.18(B) must be used first. Nameplate Amps, rather than VA, properly sizes the hot conductors.
3.8 x 1.25 for continuous load = 4.75A each, 4 lights per 20A Circuit.
Finally harmonics are considered on the neutral, per 210.61(C) Informational note, which may require some engineering assistance.