Please suggest how to reconcile the following two Code passages, that seem to differ as to current on a service entrance neutral:
From Handbook Commentary following 240.4, quote:
"The increased ratings given in Table 310.15(B)(6) are based on the significant diversity inherent to most dwelling unit loads and the fact that only the two ungrounded service or feeder conductors are considered to be current carrying."
(underlining added)
in contrast to:
From 220.61, quote:
"The feeder or service neutral load shall be the maximum unbalance of the load determined by this article. "
From Handbook Commentary following 240.4, quote:
"The increased ratings given in Table 310.15(B)(6) are based on the significant diversity inherent to most dwelling unit loads and the fact that only the two ungrounded service or feeder conductors are considered to be current carrying."
(underlining added)
in contrast to:
From 220.61, quote:
"The feeder or service neutral load shall be the maximum unbalance of the load determined by this article. "
Thanks , --ToolHound