Can you rephrase the question?
I was told that the neutral had come down to where the hot ties into the breaker then back up to the neutral bar.Can you rephrase the question?
I was told that the neutral had come down to where the hot ties into the breaker then back up to the neutral bar.
I HATE it when people do that.Now what would be a good typical practice, at least in today's panels that generally have space, is making the hot long enough to reach any breaker position in the panel. I don't think it warrants a rule though.
Now what would be a good typical practice, at least in today's panels that generally have space, is making the hot long enough to reach any breaker position in the panel. I don't think it warrants a rule though.
I HATE it when people do that.
300.20 Induced Currents in Ferrous Metal Enclosures
or Ferrous Metal Raceways.
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be ar-
ranged so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Sounds like they're interpreting this:
IMO unless they want to define exactly what grouped together means this should be removed from the NEC.
There are folks out there that will leave spare lengths of wire in a panel. They will pull wires long enough to reach the bottom of the panel, make loops, dipsy doodles, mickey mouse ears, etc to use up the slack before landing on the breaker.I have never even seen it done.
Thereby bringing to an end the universe as we know it?...afraid someone might have to use a wirenut in the panel if something were to change.
Or at least a total collapse of everything we know to be within the bounds of good taste.:jawdrop:Thereby bringing to an end the universe as we know it?
Using a very broad interpretation, on the same planet is grouped together... :lol:IMO unless they want to define exactly what grouped together means this should be removed from the NEC.
I HATE it when people do that.
Why? What would be the point?
Thereby bringing to an end the universe as we know it?