One of the C-phase cables on a Switchboard was below the NETA standard of 100 Mega ohms (the cable read 20 Mega ohms. We were planning to replace 3 sets of 4 cables but the concern came up that one of the cable bundles is stuck due to heaved conduits.
So my thought is to swap the Phase-C and neutral cables at both ends in one conduit. This way Phase-C will have all three good cables and the neutral will end up with one problematic cable. The neutral leg has hardly any current (only the imbalanced current from lighting load).
I would like to hear your thoughts if this would be fine or if it would compromise safety.
So my thought is to swap the Phase-C and neutral cables at both ends in one conduit. This way Phase-C will have all three good cables and the neutral will end up with one problematic cable. The neutral leg has hardly any current (only the imbalanced current from lighting load).
I would like to hear your thoughts if this would be fine or if it would compromise safety.