Neutral issue. Don't be that person.

Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Don't trust the POCO or the previous EC.

House just a couple years old has had issues since day one. EC says my side is good. Area POCO says all good on his side.

Recently a new building added to the sight and it was discovered the neutral had never been connected at the POCO pad mount secondary.

How in the holy hell do you miss that from day one?

Pictures when I get one.
 
View attachment 2581552
Not quite what I envisioned. Guessing the EC put neutral in lug but factory connection of lug to buss was substandard. Still, how the heck do you miss this when neutral problems have been evident almost from the beginning?
With no marks where there was arcing, it almost looks like it was never attached
 
How can your crap even work they would be blowing thing in there home left and right— EC fault and power company—- and the inspector! Shows your money going to the government really pays
 
Top