There are various lugs available for new panelboards/load centers but it is questionable whether they will fit a brand they were not intended for. For example a qo70ancp requires a specific hole center to center distance. You could also add or replace the neutral bar. Google "neutral bar kit".I am powering a sub panel out of an old ITE panel. There are no lugs on the neutral bar big enough for the wire I am adding(#2). How do I address this on a panel this old? Are there universal neutral lug adapters?
Done that before.If you can't find the correct lug, just split bolt/Polaris to the neutral conductor.
Glad you brought that up. Besides a 110.3 is there another reference that would be used? I have seen that many times over the years.The electrician in this panel previously faced the same issue. His solution was to split the copper strands in two groups, each group gets its own neutral screw. Plenty safe but I doubt NEC compliant.
I admit I don't like doing that from an aesthetic standpoint, but can't really think of any code violation. There is nothing that says a conductor must be terminated using "factory stranding" or anything like that. I could see having to show the new conductor size made which might be difficult. We form our own conductor when we twist SEU, so I don't see why splitting it into two groups would make any difference.Glad you brought that up. Besides a 110.3 is there another reference that would be used? I have seen that many times over the years.
Thanks
...His solution was to split the copper strands in two groups, each group gets its own neutral screw. Plenty safe but I doubt NEC compliant.
...I have seen that many times over the years.
Yeah I did see thatFeel free to laugh but if you look at the top of the pic in my post #7, you will see somebody 35-40 years ago doing exactly that with an aluminum gnd from another SE cable, fanning it out into multiple (actually 3) screws. Of course it works, but...
I am not a real electrician, so I'd leave the debate up to you all to figure out if that's an actual violation.