If your measurements of the A and B leg of the phase are accurate, then I guarantee you that 22A is making it back to the transformer neutral point. The question is how many paths is it taking and what are they.Was measuring amperage for 120/240V panel
Line side - Phase A: 11A, Phase:B 32A
But the Neutral was only carrying: 9A, why would it not be carrying around 22A?
Maybe not if the area has a common metal underground water piping system and multiple services are bonded to that system as required by the code. It is not unusual to find 20% or more of the neutral current on the water system even where the neutral is in perfect shape. You can have a completely open service neutral without any voltage mismatch where the metal water pipe is carrying the neutral current.If your measurements of the A and B leg of the phase are accurate, then I guarantee you that 22A is making it back to the transformer neutral point. The question is how many paths is it taking and what are they.
But I don't think your measurements are accurate. Assuming you checked for voltage and both legs were 120v to neutral, it would mean that you have an alternative path back to the transformer that is better than the intended neutral by being able to carry more than half of the current.
It would make sense if you had a bad neutral, but then you would see a voltage mismatch between the legs and neutral.
Was measuring amperage for 120/240V panel
Line side - Phase A: 11A, Phase:B 32A
But the Neutral was only carrying: 9A, why would it not be carrying around 22A?
I checked the voltage everywhere and got correct voltagesIf your measurements of the A and B leg of the phase are accurate, then I guarantee you that 22A is making it back to the transformer neutral point. The question is how many paths is it taking and what are they.
But I don't think your measurements are accurate. Assuming you checked for voltage and both legs were 120v to neutral, it would mean that you have an alternative path back to the transformer that is better than the intended neutral by being able to carry more than half of the current.
It would make sense if you had a bad neutral, but then you would see a voltage mismatch between the legs and neutral.
I check GEC too and it only had 3-4 amps.Check the current on the GEC.
I'm not concerned about the 240v. I'm curious about why I'm not getting the difference sent back to my neutral.Because none of your 240V loads will have current on the neutral.
I don't know then what the issue is, but it's physics. Your original thoughts are solid.I checked the voltage everywhere and got correct voltages
You going to have to show me that math for that based on the values in post #1. I don't see any possible combination of line to line and line to neutral loads that would result in 9 amps of neutral current where one line is carrying 11 amps and the other 32 amps.230710-1933 EDT
shk1101:
chris kennedy answered your question in post #2.
.
Clamp all the incoming conductors at the same time. What is it?
I'm not concerned about the 240v. I'm curious about why I'm not getting the difference sent back to my neutral.