The problem with the measurement is that in a main panel, where the neutral and ground are bonded, you cannot just clamp the neutral to the meter and get a complete measurement because there are other paths available via any ground path. In the main panel, you would need to clamp all the individual branch circuit neutrals. If it is a subpanel, you can clamp the neutral and get an accurate reading.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
I check GEC too and it only had 3-4 amps
that is the amount of current you'd have flowing with a bolted fault L to ground if the ground rod was a little iffy (30 ohms)

A 120 volt leg connected directly to a 25 ohm ground electrode would only flow 4.8 amps
 
Last edited:

retirede

Senior Member
Location
Illinois
that is the amount of current you'd have flowing with a bolted fault L to ground if the ground rod was a little iffy (30 ohms)

A 120 volt leg connected directly to a 25 ohm ground electrode would only flow 4.8 amps

That’s only true if the only GEC path terminates in the earth. If the grounding electric system includes, for example, a water pipe connected to a municipal water system, the GEC could carry the entire neutral load.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
That’s only true if the only GEC path terminates in the earth. If the grounding electric system includes, for example, a water pipe connected to a municipal water system, the GEC could carry the entire neutral load.
Yeah I have seen that. But the point is, he has 3-4 amps on the grounding electrode conductor. Seems kind of excessive

I'm thinking high impedance neutral
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Well you should be.

Because none of your 240V loads will send *anything* back on the neutral.

Just based on the numbers you have posted, you could theoretically have 10 amps of 240V loads, 12 amps of 120 L-N loads, with 9A on the neutral and 3 on the EGC.


All I’m going off of is the numbers. You haven’t told us anything about the existing loads.
if he has 10 amps of line to line loads, he would have 1 amp of line to neutral load on line A, and 22 amps of line to neutral load on line B, making the neutral current 21 amps.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Maybe there is a bond or bonds carrying the other 7 amps
About the only outside path for that amount of current would be a common metal underground water piping system. That could occur with a neutral to interior metal water pipe bond on the load side of the main bonding jumper. Such current would show on the water pipe. but not the GEC.
The OP needs to check the current on the water pipe itself.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
230715-1646 EDT

shk1101:

Can you approximately replicate your measurements of post #1:

If so, then there are several things to try.

First, verify that this is source from a single phase. If it is, then ( L1-N ) + ( L2-N ) will equal ( L!- L2 ) where - equals to.

Repeat your original experiment.

Open all two pole breakers except the main.

Open all single phase L2 breakers, L2 should read 0 current, and close all L1 single phase breakers. L2 should read 0 current, and L1 and neutral should both read the same.

Open all single phase L1 breakers, L1 should read 0 current, and close all L2 single phase breakers. L1 should read 0 current, and L2 and neutral should both read the same.

Open all single pole breakers, and close all 2 pole breakers. Measure L1, L2, and neutral currents.

Presents your results.

.
 