We have a 54 KW boiler, 240 single phase that is continuous duty which is 281 amps. Will feed with (2) 300 KCMILL conductors on 300 amp OCPD. There is a small neutral load of less than 3 amps. Can the neutral of a branch circuit be reduced in size from the phase conductors. If so where is it in the NEC?