Heres the system overview as I have it so far.
2x SolarEdge Se33.3k inverters
218 Hanwa 315 QPro modules
Hooking up to a 240v High leg service
The question is in finding a legal interconnection betweeen the 480 wye output of the inverters and the 240v high leg service.
I tried getting a hold of the POCO to see if they would allow a connection to the AC phases and ignoring the B phase like has been suggested (and just using 1 phase inverters) but nobody at Rocky Mtn Power was able to give me an answer. The SolarEdge guys dont seem to know much about this service and they recommended trying the single phase route across the phases or just going all on the A and C phases. Again this depends on if the POCO approves...
We will have an EE look over everything before we submit the interconnetion application.
You'll need to get a transformer that is 277/480WYE (inverters) on one side, and 120/240 Delta on the other side (building grid). There is no way to connect the 33.3k inverters directly to any other grid than 277/480.