James L
Senior Member
- Location
- Kansas Cty, Mo, USA
- Occupation
- Electrician
It would be like connecting the neutral to a metal conduit1. Enclosure is not allowed to carry the neutral current. If you land the neutral on the cabinet ground bus the neutral current would have to travel on the enclosure to get back to the service neutral. No different than trying to use the grounding conductor as the neutral.