Nothing on that drawing indicates that a neutral is required. #1/0 for 300 amps is incorrect.because it's 3Phase 4W panel and 3 P breaker correct?
2 sets of 1/0.Nothing on that drawing indicates that a neutral is required. #1/0 for 300 amps is incorrect.
You only need to install a neutral if that panel has line to neutral loads. A 3P 4W panel does not require a neutral if there are no line to neutral loads.Here's the remainder of loads/one line.. MDP and LP panels. There's has to be L to N loads..lol.
And if your feeding a 3P 4W panel you'd need the neutral. Feed to LP has no neutral.
Thanks. How do know if a load is line to neutral?You only need to install a neutral if that panel has line to neutral loads. A 3P 4W panel does not require a neutral if there are no line to neutral loads.
Don't understand what your asking. The continuation is in post #4.Is the feeder in post #1 feeding a 1Ø, feeder? If so then the neutral is there.
So this is panel LP-1? Is there a tap in what appears to be a wireway?The continuation is in post #4.
Are there any single pole breakers?Thanks. How do know if a load is line to neutral?
How are you getting 120/240V single phase in the Power Riser Diagram from a 208/120V three phase service?Here's the remainder of loads/one line.. MDP and LP panels. There's has to be L to N loads..lol.
And if your feeding a 3P 4W panel you'd need the neutral. Feed to LP has no neutral.
View attachment 2575847
View attachment 2575846
He's not. The distribution panel (MCP) shows single phase, 120/208 volt panels.How are you getting 120/240V single phase in the Power Riser Diagram from a 208/120V three phase service?
Single-pole breaker, or a 2- or 3-pole breaker feeding a load with a neutral conductor.Thanks. How do know if a load is line to neutral?
There appear to be, at the very bottom, (4) 1-pole breakers.Are there any single pole breakers?
Sorry. Yellow are new circuits. So below is the one line, panel MDP( which feds sub panels) and one sub panel schedule.This certainly would have been easier to address if the first post contained all relevant information!
On the Power Riser Diagram it shows "MDP1 250AMP 120/208Y 3 PHASE MAIN BREAKER" feeding "2C SUB PANEL 120/240 1 PHASE MAIN LUG". Does that just mean the panel is 240V rated but the circuits will all be 208/120V single phase?He's not. The distribution panel (MCP) shows single phase, 120/208 volt panels.
Yes it will be supplied by 120/208. I'm guessing that the panel is rated for 120/240 as you've stated.Does that just mean the panel is 240V rated but the circuits will all be 208/120V single phase?